Anode Rod Passivation Question

The Tank Anode Rod Passivation Question

Viewing 11 posts - 1 through 11 (of 11 total)
  • Author
    Posts
  • #24206
    ODA
    Participant

    Situation: Moved into my current house approximately 5 years ago. Never had soft water. There was a non-functioning, broken water softener on the side of the house, but I didn’t hook it up or repair it. The city water supply is definitely hard.

    The water heater I inherited is a direct vent Ruud, manufactured in 2010. According to the manufacturer, it had a six year warranty. It has only the original manufacturers anode, which in Ruud’s case, is a non-accessible magnesium anode, with no “bump” on the hex head.

    There was no aftermarket combination anode rod installed.

    I decided to check the status of the anode rod, so I cut through the sheet metal top to gain access to it.

    Upon pulling out the anode (partially, due to lack of overhead clearance), to my untrained, inexperienced eye, it appeared that this anode was not sufficiently corroded. I assumed that the anode rod would be very corroded. Instead, it appears to be pretty clean and non-corroded, for being in hard water for about 8 years.

    Question: Is this anode rod passivated?

    I am attaching photos to assist in diagnosing this.

    Thank you.

    Attached files

    #24207
    ODA
    Participant

    Top View

    Attached files

    #24208
    ODA
    Participant

    Anode coming out.

    Attached files

    #24209
    ODA
    Participant

    Anode Rod.

    Attached files

    #24210
    ODA
    Participant

    Anode Rod 2

    Attached files

    #24211
    ODA
    Participant

    Anode Rod 3

    Attached files

    #24212
    Larry Weingarten
    Participant

    Hi, It looks at least partly passivated to me. The resistor in the top of the anode seems to work a bit too well. After eight years in hard water it should be largely gone. I’d replace it with a non-resistored, flex anode after having a look around the tank and in the combustion chamber to make sure there isn’t already a leak. 😎

    Yours, Larry

    #24213
    ODA
    Participant

    The flex anodes you sell are non-resistored, correct?

    #24214
    ODA
    Participant
    #24215
    Larry Weingarten
    Participant

    Hello, Randy can answer that better than me, but I’m quite sure they have no resistor. 😎

    Yours, Larry

    #24216
    Randy Schuyler
    Keymaster

    That is correct.

    Randy Schuyler